Omit, note as directed by Architect, and submit.
If bounced, submit COR.
Only question to ask the Architect, if bounced, is clean agent or A.S. (wet
or PA?) (or both CA and AS) to be included in the COR, and who's got the
detection?

This is one where it may be wise to simply confirm direction from Arch in
writing, and play dumb installing contractor. After all, they're the
Professionals.

You could, if you desire to minimize schedule impact, copy the AHJs on the
confirmation to the Architect to telegraph the blow. 

Glc
PS- John Marshall, first chief justice of the US Supreme Court, has 2 L's.
Fire marshals do not rise to that.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Thursday, August 02, 2007 8:27 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

The design criteria on the drawings are:
1. International Fire Prevention Code with North Carolina Amendments
2. NFPA-13
3. Local Fire Marshall
4. County Building Officials 


 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Thursday, August 02, 2007 8:10 AM
To: [email protected]
Subject: RE: Telecom & Data Rooms

Brian,

What is the adopted building code in this jurisdiction ?   That's the
starting point.

John Drucker 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Thursday, August 02, 2007 8:06 AM
To: [email protected]
Subject: Telecom & Data Rooms

I'm being told by an Architect we are doing a school with that I need to
remove any heads from the Telecom & Data rooms and that I'm not allowed to
run any pipe above those ceilings either. He is basing it on the provisions
for eliminating heads in and Electrical room with a 2 hour fire wall, am I
missing something? I am not aware of Telecom & Data rooms falling into the
same category as an Electrical room. I have approved plans from the AHJ with
the heads shown in those rooms and omitted from the Electrical rooms. Any
thoughts?
 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to