In designing an ESFR system the following is one of the FM requirements;
>2.2.6.1 Coordinate the location of sprinklers and the design of powered >heating, ventilation and air conditioning >for buildings protected by suppression mode sprinklers so that the air >velocity at sprinklers does not >exceed 5 ft/sec (1.52 m/sec). I am required, according to job specifications, to design to NFPA-13. I don't see such a requirement in NFPA-13 or in the listing of the sprinkler. Am I missing something? The Insurance agent is now throwing the above section from FM at us. Suggestions/comments, please. Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)