While I realize the CONTRACTUAL differences -and cost impact that should be,
from what was presented here, recoverable as a change (increase) in scope
post-bid, I certainly think that FM's requirements on ESFR are probably the
most accurate, being based on test data, field experience, and they are not
muddied by the process required of the minimum concensus standard that can
change pure engineering data and recommendations based upon it.

Certainly there is a diffference between code and FM Global recommendations,
but when it comes to ESFR, I think FM wrote the book and I'd be careful when
deviating from their bible. Sure, cost impacts need to be included, but an
intelligent Owner should agree to the extras, or at least consider them. 

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, September 05, 2007 10:02 AM
To: [email protected]
Subject: RE: ESFR heads at airflow openings

Ok, so do you have roof or sidewall exhaust fans?   Any intake plenums
with diffusers, or just an open intake?  What are the sizes of the fan
intakes?

If the fans are roof mounted is the opening level with the underside of the
roof (no plenum), and what relative distance is there (vertically) between
the sprinkler and intake?



Some AHJ's and others think that meeting FM is required just like it's
another Code.  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to