A potential "back door" gotcha is.. Some years ago there were some ESFR
sprinklers that had FM approval only. If I remember right, there is usually
a little box in the approval section of the Tech Data sheet that states that
in order to have FM approval, this sprinkler must be installed in accordance
with 2-2.

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, September 05, 2007 9:02 AM
----- >To: [email protected]
----- >Subject: RE: ESFR heads at airflow openings
----- >
----- >Ok, so do you have roof or sidewall exhaust fans?   Any 
----- >intake plenums
----- >with diffusers, or just an open intake?  What are the 
----- >sizes of the fan intakes?
----- >
----- >If the fans are roof mounted is the opening level with 
----- >the underside of the roof (no plenum), and what relative 
----- >distance is there (vertically) between the sprinkler and intake?
----- >
----- >
----- >
----- >Some AHJ's and others think that meeting FM is required 
----- >just like it's another Code.  
----- >
----- >
----- >Craig L. Prahl, CET
----- >Fire Protection Group
----- >Mechanical Department
----- >CH2MHILL
----- >Lockwood Greene
----- >1500 International Drive
----- >PO Box 491, Spartanburg, SC  29304-0491
----- >Direct - 864.599.4102
----- >Fax - 864.599.8439
----- >[EMAIL PROTECTED]
----- >http://www.lg.com
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Bobby Gillett
----- >Sent: Wednesday, September 05, 2007 9:37 AM
----- >To: [email protected]
----- >Subject: RE: ESFR heads at airflow openings
----- >
----- >The insurance carrier is not FM he is just quoting FM 
----- >and the GC spec's did not require FM only NFPA-13. I 
----- >just wanted to have my ducks in a row before I responded.
----- >
----- >They already had the HVAC Eng. calculate the airflow and 
----- >they say it requires me to be 30" from the edge of all 7 
----- >of the exhaust fans (for heat removal--no AC). My 
----- >thinking was in line with yours Craig, if all of the 
----- >sudden they want to follow FM - that would be a change 
----- >to perform the work.
----- >
----- >One of the resolutions, according to FM, is as follows;
----- >
----- >2.2.6.2 If it is not possible to meet 2.2.6.1, chose one 
----- >of the following
----- >>options to ensure proper operation
----- >>of suppression mode sprinklers in buildings with ceiling-level
----- >ventilation:
----- >>
----- >>
----- >>a) Sprinklers Beneath Vent Openings
----- >>
----- >>Install suppression mode sprinklers of the same type 
----- >used elsewhere in 
----- >>the building centered in vent openings having a maximum 
----- >dimension of
----- >>4.5 ft (1.37 m). This option does not apply to storage 
----- >of commodities 
----- >>greater in hazard than cartoned unexpanded plastic, 
----- >such as uncartoned 
----- >>plastic, aerosols or rolled tissue in buildings higher 
----- >than 30 ft (9.14
----- >
----- >>m).
----- >
----- >I would have to put a sprinkler in the vent opening, due 
----- >to spacing there is no way to move over and be 30" away. 
----- >I believe this would act like an obstruction and the one 
----- >we added would not have an affect on the other sprinkler 
----- >spacing-correct?
----- >
----- >Bobby Gillett
----- >Project Manager
----- >[EMAIL PROTECTED]
----- >(731)-424-0130
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, September 05, 2007 8:27 AM
----- >To: [email protected]
----- >Subject: RE: ESFR heads at airflow openings
----- >
----- >The closest thing to that requirement is the table 
----- >8.3.2.5(a) which is dealing with temperature of heads in 
----- >relation to heat sources, not specifically ESFR and air 
----- >velocity.  Other than that I couldn't find anything 
----- >related to adjacent air velocities.  (I've got 
----- >electronic search capabilities)
----- >
----- >First thing I'd do is go back to the GC and state that 
----- >your contract directs you to design to NFPA NOT FM.  If 
----- >the client wants to adhere to FM standards and did not 
----- >indicate that in any of the project bid documents then 
----- >any extra effort required on your part to meet those 
----- >requirements should be an add to your contract.
----- >
----- >If you're using ESFR, are you in a open ceiling 
----- >warehouse or mfg. space?
----- >If that's the case most of your air distribution is 
----- >probably below your sprinklers and if so, the discharge 
----- >velocity of the diffusers should be inconsequential to 
----- >your sprinklers as they should be discharging air 
----- >downward.  If you have areas where there are either 
----- >intake or exhaust louvers or diffusers and they look 
----- >like they will draw air across your sprinklers then 
----- >you'll need the HVAC plans showing the discharge 
----- >information on those outlets so you can space heads 
----- >accordingly.  But even with that, it's really not up to 
----- >the sprinkler contractor to determine what the air 
----- >velocity is at a given point in space.  You as the 
----- >sprinkler contractor shouldn't have to undergo the 
----- >exercise of determining when the air velocity drops to 
----- >or below 5 fps.
----- >
----- >Other question is, does the FM guy know what the 
----- >terminal velocities are of the air devices in relation 
----- >to the location of your sprinklers?
----- >
----- >
----- >Craig L. Prahl, CET
----- >Fire Protection Group
----- >Mechanical Department
----- >CH2MHILL
----- >Lockwood Greene
----- >1500 International Drive
----- >PO Box 491, Spartanburg, SC  29304-0491
----- >Direct - 864.599.4102
----- >Fax - 864.599.8439
----- >[EMAIL PROTECTED]
----- >http://www.lg.com
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Bobby Gillett
----- >Sent: Wednesday, September 05, 2007 8:27 AM
----- >To: [email protected]
----- >Subject: ESFR heads at airflow openings
----- >
----- >In designing an ESFR system the following is one of the 
----- >FM requirements;
----- >
----- > 
----- >
----- > >2.2.6.1 Coordinate the location of sprinklers and the 
----- >design of powered
----- >
----- >>heating, ventilation and air conditioning
----- >
----- >>for buildings protected by suppression mode sprinklers 
----- >so that the air
----- >
----- >>velocity at sprinklers does not
----- >
----- >>exceed 5 ft/sec (1.52 m/sec).
----- >
----- > 
----- >
----- >I am required, according to job specifications, to 
----- >design to NFPA-13. I don't see such a requirement in 
----- >NFPA-13 or in the listing of the sprinkler.
----- >Am I missing something? The Insurance agent is now 
----- >throwing the above section from FM at us. 
----- >Suggestions/comments, please.
----- >
----- > 
----- >
----- >Bobby Gillett
----- >
----- >Project Manager
----- >
----- >[EMAIL PROTECTED]
----- >
----- >(731)-424-0130
----- >
----- > 
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to