I have seen? the sprinkler pipe protected?with 2 hours material;or provide 
sprinklers along the piping.There is some wording in NFPA 13.
mario berrios
[EMAIL PROTECTED]


-----Original Message-----
From: Todd Williams - FPDC <[EMAIL PROTECTED]>
To: [email protected]
Sent: Wed, 10 Oct 2007 4:48 am
Subject: sprinkler piping in unsprinklered areas


A facility has a 20,000 sqft area, which is sprinklered. Attached to that is a 
12,000 sqft unsprinklered addition (which the owner is not going to sprinkler). 
Attached to that is to be a new 30,000 sqft addition, which is to be 
sprinklered. The service comes in to the 20,000 section. The sprinkler main 
will need to run through the unsprinklered addition in order to get to the new 
area. Is there any issue with this? I was once told something running pipe in 
unprotected areas, but can't find anything in NFPA. (I know, we do it above 
ceilings all the time, but what about this situation?)?
?
To make matter worse, this is a plastics manufacturing facility. The owner 
thinks everything they do is Light Hazard at worst and doesn't like sprinklers. 
The AHJ would approve a coloring book if it had a PE stamp.?
?
Todd G. Williams, PE?
Fire Protection Design/Consulting?
Stonington, Connecticut?
www.fpdc.com?
860.535.2080 _______________________________________________?
Sprinklerforum mailing list?
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum?
?
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)?


________________________________________________________________________
Email and AIM finally together. You've gotta check out free AOL Mail! - 
http://mail.aol.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to