Isn't there an assumption made by NFPA 13 that the building is protected in
accordance with the standard?  The standard states that the building is
provided with automatic sprinkler protection?  So would NFPA need to address
piping in a non-sprinklered area when it assumes the building is a
sprinklered area.

Just looking at the sizes of the space, has the AHJ agreed to have the
unsprinklered addition?  Is the area separated by a fire wall?  My thought
is you have to install sprinklers in that area to protect the piping.

Just my random thoughts, I don't have big code to back it up.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Wednesday, October 10, 2007 4:48 AM
To: [email protected]
Subject: sprinkler piping in unsprinklered areas

A facility has a 20,000 sqft area, which is sprinklered. Attached to 
that is a 12,000 sqft unsprinklered addition (which the owner is not 
going to sprinkler). Attached to that is to be a new 30,000 sqft 
addition, which is to be sprinklered. The service comes in to the 
20,000 section. The sprinkler main will need to run through the 
unsprinklered addition in order to get to the new area. Is there any 
issue with this? I was once told something running pipe in 
unprotected areas, but can't find anything in NFPA. (I know, we do it 
above ceilings all the time, but what about this situation?)

To make matter worse, this is a plastics manufacturing facility. The 
owner thinks everything they do is Light Hazard at worst and doesn't 
like sprinklers. The AHJ would approve a coloring book if it had a PE stamp.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to