A facility has a 20,000 sqft area, which is sprinklered. Attached to
that is a 12,000 sqft unsprinklered addition (which the owner is not
going to sprinkler). Attached to that is to be a new 30,000 sqft
addition, which is to be sprinklered. The service comes in to the
20,000 section. The sprinkler main will need to run through the
unsprinklered addition in order to get to the new area. Is there any
issue with this? I was once told something running pipe in
unprotected areas, but can't find anything in NFPA. (I know, we do it
above ceilings all the time, but what about this situation?)
To make matter worse, this is a plastics manufacturing facility. The
owner thinks everything they do is Light Hazard at worst and doesn't
like sprinklers. The AHJ would approve a coloring book if it had a PE stamp.