Go back to the building code, that's the starting point.  

John Drucker
Fire Protection Subcode Official
New Jersey 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, October 10, 2007 9:50 AM
To: [email protected]
Subject: RE: sprinkler piping in unsprinklered areas

What is the unsprinklered area used for?  What is the usage of the other
two areas?

The closest verbiage relating to protecting fire protection piping is in
NFPA 14, 6.1.2.2, related to standpipes outside of protected stairways,
since you could have standpipes where no sprinklers are present.  I've
searched NFPA 13 and couldn't find anything relating to the protection
of sprinkler lines running through nonprotected areas.  The closest
thing there is related to private service mains in hazardous areas,
(8.16.4.3).  You might be able to use that based on the similarity of
the intent but might have problems due to the actual definition of the
private service main.  I'll have to agree that the code probably assumes
if there are sprinklers present that the area is protected.

I guess the question is whether or not the walls separating the
protected from nonprotected areas are code compliant for the listed
occupancies.  Are they rated fire walls in accordance with the
applicable building/fire code, are there listed door assemblies between
the areas, questions, questions, questions.  

If a fire broke out in the nonprotected area and the building structure
failed, it will most likely take out the fire main and disable the
entire facility.  Is the owner aware of this possibility.  

Do you have an insurance underwriter or state/local fire marshal to work
with?


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael
O'Brian
Sent: Wednesday, October 10, 2007 9:09 AM
To: [email protected]
Subject: RE: sprinkler piping in unsprinklered areas

Isn't there an assumption made by NFPA 13 that the building is protected
in accordance with the standard?  The standard states that the building
is provided with automatic sprinkler protection?  So would NFPA need to
address piping in a non-sprinklered area when it assumes the building is
a sprinklered area.

Just looking at the sizes of the space, has the AHJ agreed to have the
unsprinklered addition?  Is the area separated by a fire wall?  My
thought is you have to install sprinklers in that area to protect the
piping.

Just my random thoughts, I don't have big code to back it up.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: Wednesday, October 10, 2007 4:48 AM
To: [email protected]
Subject: sprinkler piping in unsprinklered areas

A facility has a 20,000 sqft area, which is sprinklered. Attached to
that is a 12,000 sqft unsprinklered addition (which the owner is not
going to sprinkler). Attached to that is to be a new 30,000 sqft
addition, which is to be sprinklered. The service comes in to the 20,000
section. The sprinkler main will need to run through the unsprinklered
addition in order to get to the new area. Is there any issue with this?
I was once told something running pipe in unprotected areas, but can't
find anything in NFPA. (I know, we do it above ceilings all the time,
but what about this situation?)

To make matter worse, this is a plastics manufacturing facility. The
owner thinks everything they do is Light Hazard at worst and doesn't
like sprinklers. The AHJ would approve a coloring book if it had a PE
stamp.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to