Go back to the building code, that's the starting point. John Drucker Fire Protection Subcode Official New Jersey
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, October 10, 2007 9:50 AM To: [email protected] Subject: RE: sprinkler piping in unsprinklered areas What is the unsprinklered area used for? What is the usage of the other two areas? The closest verbiage relating to protecting fire protection piping is in NFPA 14, 6.1.2.2, related to standpipes outside of protected stairways, since you could have standpipes where no sprinklers are present. I've searched NFPA 13 and couldn't find anything relating to the protection of sprinkler lines running through nonprotected areas. The closest thing there is related to private service mains in hazardous areas, (8.16.4.3). You might be able to use that based on the similarity of the intent but might have problems due to the actual definition of the private service main. I'll have to agree that the code probably assumes if there are sprinklers present that the area is protected. I guess the question is whether or not the walls separating the protected from nonprotected areas are code compliant for the listed occupancies. Are they rated fire walls in accordance with the applicable building/fire code, are there listed door assemblies between the areas, questions, questions, questions. If a fire broke out in the nonprotected area and the building structure failed, it will most likely take out the fire main and disable the entire facility. Is the owner aware of this possibility. Do you have an insurance underwriter or state/local fire marshal to work with? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Michael O'Brian Sent: Wednesday, October 10, 2007 9:09 AM To: [email protected] Subject: RE: sprinkler piping in unsprinklered areas Isn't there an assumption made by NFPA 13 that the building is protected in accordance with the standard? The standard states that the building is provided with automatic sprinkler protection? So would NFPA need to address piping in a non-sprinklered area when it assumes the building is a sprinklered area. Just looking at the sizes of the space, has the AHJ agreed to have the unsprinklered addition? Is the area separated by a fire wall? My thought is you have to install sprinklers in that area to protect the piping. Just my random thoughts, I don't have big code to back it up. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Wednesday, October 10, 2007 4:48 AM To: [email protected] Subject: sprinkler piping in unsprinklered areas A facility has a 20,000 sqft area, which is sprinklered. Attached to that is a 12,000 sqft unsprinklered addition (which the owner is not going to sprinkler). Attached to that is to be a new 30,000 sqft addition, which is to be sprinklered. The service comes in to the 20,000 section. The sprinkler main will need to run through the unsprinklered addition in order to get to the new area. Is there any issue with this? I was once told something running pipe in unprotected areas, but can't find anything in NFPA. (I know, we do it above ceilings all the time, but what about this situation?) To make matter worse, this is a plastics manufacturing facility. The owner thinks everything they do is Light Hazard at worst and doesn't like sprinklers. The AHJ would approve a coloring book if it had a PE stamp. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)