Not in the '07 - 7.2.3.1 - You use the manifold in lieu of the program.  And
only use the program OR manifold if greater than 500 or 750 gal. The program
indicates compliance without any ITV so a single head should suffice.  You
do not have to confirm the program with a field test.  That would be like
opening the heads in the RA and measuring flow to prove the calculations
work.   I don't believe the manifold is technically in the '02.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Wednesday, October 10, 2007 2:33 PM
To: [email protected]
Subject: RE: Dry system size

You only use/install the manifold if you are calculating the trip time with
a program. If you are not you will have a single inspectors test.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Wednesday, October 10, 2007 1:28 PM
To: [email protected]
Subject: RE: Dry system size

Okay, what about the test manifold? When is that to be utilized?

Ron

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to