So if I choose option #3, I do not have to use option #2 involving a program or use #1 and meet it's requirement of a single connection with 60 sec. time period. #3 means using a test manifold using table 7.2.3.6.1. This table shows (in my situation for ordinary hazard) to use a two outlet manifold utilizing one branch line and a water delivery time of 50 seconds.
Ron -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, October 11, 2007 11:16 AM To: [email protected] Subject: Re: Dry system size lets start over again and allow me to summarize what has been said by others. For systems greater than 750 gals, you have THREE options. 1. Single test connection at 60 seconds 2. Calculated delivery using Table 7.2.3.6.1 3. Test manifold using Table 7.2.3.6.1 Read 7.2.3.7 taking note of the last sentence (confirming if you use the manifold you do not have to do either of the other two options). This section also tells you where to connect when more than 2 sprinklers are on the manifold. Other tidbits: Even with a calculated system, you still have to do the single head flow test as part of the acceptance test BUT there is NO 60 sec limit. For smaller systems serving a dwelling unit, you now have to satisfy the 60 sec rule (for spray sprinklers). Roland On Oct 10, 2007, at 1:45 PM, Russell wrote: > I take it that the table 7.2.3.6.1 goes only with a program, but if > so, how > do I determine the number of branch lines to include in the > manifold? Am I > not understanding what you're telling me? > > Ron > > Internal Virus Database is out-of-date. > Checked by AVG Free Edition. > Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: > 6/10/2007 > 1:39 PM > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
