That is good info, I will use that.

Bill Minkel
Designer
Western States Fire Protection Dallas 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, October 11, 2007 10:16 AM
To: [email protected]
Subject: Re: Dry system size

lets start over again and allow me to summarize what has been said by
others.

For systems greater than 750 gals, you have THREE options.
1. Single test connection at 60 seconds
2. Calculated delivery using Table 7.2.3.6.1 3. Test manifold using Table
7.2.3.6.1

Read 7.2.3.7 taking note of the last sentence (confirming if you use  
the manifold you do not have to do either of the other two options).   
This section also tells you where to connect when more than 2 sprinklers are
on the manifold.

Other tidbits:
Even with a calculated system, you still have to do the single head flow
test as part of the acceptance test BUT there is NO 60 sec limit.
For smaller systems serving a dwelling unit, you now have to satisfy the 60
sec rule (for spray sprinklers).

Roland

On Oct 10, 2007, at 1:45 PM, Russell wrote:

> I take it that the table 7.2.3.6.1 goes only with a program, but if 
> so, how do I determine the number of branch lines to include in the 
> manifold? Am I not understanding what you're telling me?
>
> Ron
>
> Internal Virus Database is out-of-date.
> Checked by AVG Free Edition.
> Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:  
> 6/10/2007
> 1:39 PM
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to