lets start over again and allow me to summarize what has been said by others.

For systems greater than 750 gals, you have THREE options.
1. Single test connection at 60 seconds
2. Calculated delivery using Table 7.2.3.6.1
3. Test manifold using Table 7.2.3.6.1

Read 7.2.3.7 taking note of the last sentence (confirming if you use the manifold you do not have to do either of the other two options). This section also tells you where to connect when more than 2 sprinklers are on the manifold.

Other tidbits:
Even with a calculated system, you still have to do the single head flow test as part of the acceptance test BUT there is NO 60 sec limit. For smaller systems serving a dwelling unit, you now have to satisfy the 60 sec rule (for spray sprinklers).

Roland

On Oct 10, 2007, at 1:45 PM, Russell wrote:

I take it that the table 7.2.3.6.1 goes only with a program, but if so, how do I determine the number of branch lines to include in the manifold? Am I
not understanding what you're telling me?

Ron

Internal Virus Database is out-of-date.
Checked by AVG Free Edition.
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to