I am spacing through currently keeping the same design all the way and treating it as no wall due to the fact it is 70% open (based on 1/2"hardware cloth-- 1/16" wire spaced 1/2" squares). I was hoping I was correct in doing so, only seeing 8.6.5.2.2 for LH!!
Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins Sent: Monday, October 22, 2007 3:33 PM To: [email protected] Subject: Re: Vertical mesh wall Bobby, If the "wall" is 70% open or more, it would not be an obstruction to sprinkler discharge. You would, however, have to extend the higher density beyond the "wall" because in terms of sprinkler operation, it would be absolutely no different than no wall. As an aside, there isn't a grocery store stock room anywhere in the real world that meets the criteria for a class IV commodity. Commodity classification is done on a pallet load/carton basis, not the overall mix in the room. If there are plastics or other higher hazard combustibles in the room, then it should be protected for that. If there is nothing worse than a class III, then that's your design. Unless it is filled with products having no more than 15% plastic in each carton or pallet load, it's not class IV. At some time of day and season of the year, any grocery store stock room is going to have lots of plastic or worse. You're not designing a sprinkler system to work some of the time. Joe Bobby Gillett wrote: > I guess my replies got lost, try again. > > > > This is Class IV comm and we have EC sprinklers (storage room in > Grocery/Shopping store). Wall of mesh keeps people out of a certain areas in > the back store room. > > > > > > Bobby Gillett > > Project Manager > > <mailto:[EMAIL PROTECTED]> > [EMAIL PROTECTED] > > (731)-424-0130 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)