Ran into an interesting mess this AM. AHJ was going to allow a building to open without alarms.
I drafted a hold-harmless, then realized that 100+ people could die, And without sufficient assets to satisfy the hold harmless, it was worthless. At $2m/death, that'd be $200M and since I've already been stiffed $50k by this character, that value exceeded the net worth and any insurance. End of Rowe Sprinkler. Time to find the AHJ and stop this nonsense. I'm happy to report that within 15 minutes of sending an email to L&I warning of a CLEAR AND PRESENT DANGER TO LIFE SAFETY, I had a section chief on the phone with his inspector on the other line in his office, assuring me that they would not allow this to happen. Good news- catastrophe averted. Scary news- back in 2003 this place was open to the public and operating under a temporary occupancy. NO ALARMS WIRED UP AT ALL. Kids broke in the back, set fire to about 500 christmas trees stored in the back, and shoppers on the other side of the wall were completely oblivious. So incredible as it may seem, >100,000 SF building, retail, open, no fire alarm hooked up at all. No wires to the flow and pressure switches, 40' high bay, and a fire going. How was this building ever allowed to operate like this? And they were going to repeat the error? FM labeled their case studies "What has Happened, Can Happen." Glad I was able to prevent a repeat in this case. So, how many other time bombs are ticking in your backyard? George Church Rowe Sprinkler _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)