Fill the space with noncombustible insulation, or build it so there is less than 6" clear between the bottom of the joists and the floor, and pick up 3,000 SF MRA in the surrounding area.
glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Haug, Marc Sent: Tuesday, October 23, 2007 11:07 AM To: [email protected] Subject: Raised Floor Altar- Dais I have a question regarding a Dais (raised floor altar) that is 18" tall and made of combustible construction. It appears to me that this is classified as a concealed space that requires sprinkler with light hazard coverage. The practicality of installing sprinklers has me wondering if the concealed spaces are limited to ceilings and above room and not on the spaces installed on a concrete floor. Any thoughts of where to look to find a way to omit these sprinklers. Marc _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)