Thanks for the clarification, Joe.  As always, you da man!

Ed Kramer
Littleton, CO



>Ed,
>
>If it is a uniform mesh that is 70% open, it's going to have no more
>effect than open web joists. If we're talking control-mode sprinklers,
>the other obstructions to distribution that are routinely allowed will
>have at least as much impact as an open wire mesh wall.
>
>Joe
>
>Ed Kramer wrote:
>> Joe,
>>
>> I believe there's a difference between mesh shelving and mesh walls.
>The
>> shelving is required to be a minimum of 18" or 36" below the sprinkler
>> deflector and in reality will be much more than that.  That distance
>allows
>> the spray pattern to fully develop, and then the droplets are falling
>> vertically through the mesh openings.  A droplet that hits a solid
>portion
>> of the mesh will still pass through in almost its original path.  There
>> ends up being no 'dry' areas below the mesh.
>>
>> NFPA's minimum sprinkler-to-wall distance is 4".  If a sprinkler were
>> installed at that distance from a mesh wall (or slightly more), do you
>> think a 30% obstructed mesh would disrupt the spray pattern development?
>> I'm not so much thinking about the mesh nearest the sprinkler, but the
>mesh
>> 30 degrees or so from perpendicular (if that makes sense).  The spray
>> pattern disruption wouldn't be that great, and that's probably why NFPA
>13
>> allows mesh privacy curtains in light hazards to be ignored.  I'd be a
>bit
>> nervous ignoring them in ordinary or storage hazards.
>>
>> OK, tell me I'll all wet (or dry, depending which side of the mesh I'm
>on).
>>
>> Ed Kramer
>> Littleton, CO
>>
>>
>>
>>> -----Original Message-----
>>> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
>>> [EMAIL PROTECTED] On Behalf Of Joe Hankins
>>> Sent: Monday, October 22, 2007 2:55 PM
>>> To: [email protected]
>>> Subject: Re: Vertical mesh wall
>>>
>>> I don't know that it is written anywhere for walls, but if rack shelves
>>> can be considered open with wire mish shelving more than 70% open, the
>>> same would go for walls.
>>>
>>> I was just responding to your statement that it was a grocery stock
>room
>>> and was class IV. If they have specified how they want it done, why are
>>> you worried about the wall?
>>>
>>> Joe
>>>
>>> Bobby Gillett wrote:
>>>
>>>> Joe,
>>>>
>>>> Thanks for your reply as well.
>>>>
>>>> I was hoping that the 70% was accurate, but could only find it applied
>>>>
>>> in
>>>
>>>> 8.6.5.2.2 as stated in an earlier response, which is for light hazard.
>>>>
>>> Is
>>>
>>>> there somewhere else that states that this applies to something other
>>>>
>>> than
>>>
>>>> LH?
>>>>
>>>> As far as the hazard classifications, this is an pre-engineered set of
>>>> drawings that has us calc'ing two different ways in the same area. The
>>>> design engineer firm wants these areas calc'd .45/2000 and .55 for the
>>>>
>>> most
>>>
>>>> 4 demanding sprinklers. That is our instruction and other than the
>town,
>>>> they are the AHJ along with the insurance company and they agree w/the
>>>> design engineer for the project. We have no storage info other than
>how
>>>>
>>> to
>>>
>>>> do it and they state in writing this is how they want it done.
>>>>
>>>> Bobby Gillett
>>>> Project Manager
>>>> [EMAIL PROTECTED]
>>>> (731)-424-0130
>>>>
>>>> -----Original Message-----
>>>> From: [EMAIL PROTECTED]
>>>> [mailto:[EMAIL PROTECTED] On Behalf Of Joe
>>>>
>>> Hankins
>>>
>>>> Sent: Monday, October 22, 2007 3:33 PM
>>>> To: [email protected]
>>>> Subject: Re: Vertical mesh wall
>>>>
>>>> Bobby,
>>>>
>>>> If the "wall" is  70% open or more, it would not be an obstruction to
>>>> sprinkler discharge. You would, however, have to extend the higher
>>>> density beyond the "wall" because in terms of sprinkler operation, it
>>>> would be absolutely no different than no wall.
>>>>
>>>> As an aside, there isn't a grocery store stock room anywhere in the
>real
>>>> world that meets the criteria for a class IV commodity. Commodity
>>>> classification is done on a pallet load/carton basis, not the overall
>>>> mix in the room. If there are plastics or other higher hazard
>>>> combustibles in the room, then it should be protected for that. If
>there
>>>> is nothing worse than a class III, then that's your design.   Unless
>it
>>>> is filled with products having no more than 15% plastic in each carton
>>>> or pallet load, it's not class IV.
>>>>
>>>> At some time of day and season of the year, any grocery store stock
>room
>>>> is going to have lots of plastic or worse. You're not designing a
>>>> sprinkler system to work some of the time.
>>>>
>>>> Joe
>>>>
>>>> Bobby Gillett wrote:
>>>>
>>>>
>>>>> I guess my replies got lost, try again.
>>>>>
>>>>>
>>>>>
>>>>> This is Class IV comm and we have EC sprinklers (storage room in
>>>>> Grocery/Shopping store). Wall of mesh keeps people out of a certain
>>>>>
>>> areas
>>>
>>>> in
>>>>
>>>>
>>>>> the back store room.
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> Bobby Gillett
>>>>>
>>>>> Project Manager
>>>>>
>>>>>  <mailto:[EMAIL PROTECTED]>
>>>>> [EMAIL PROTECTED]
>>>>>
>>>>> (731)-424-0130
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>>>>
>>> [EMAIL PROTECTED]
>>>
>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>>
>>>>>
>>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>>>
>>> [EMAIL PROTECTED]
>>>
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>>>
>>> [EMAIL PROTECTED]
>>>
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>>
>>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> To Unsubscribe, send an email to:Sprinklerforum-
>[EMAIL PROTECTED]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to