George,

I think you have a 13D. IBC 2006 (out West we're progressive so we
burnt our 2003s) R-2 is for, "...apartment houses, boarding houses
(non-transient)...dormitories, fraternities...monasteries...." Your's
is obviously one of these but there's a caveat, "Congregate living
facilities with 16 or fewer occupants are permitted to comply with the
construction requirements for group R-3." R-3 is for, among other
things, "Congregate living facilities with 16 or fewer persons." R3 is
also for, "Buildings that do not contain more than two dwelling
units." You are a 13D. As important as what you is is what you ain't
and you ain't an R-1 which are essentially sleeping quarters for
transients (makes those rich folks that live year round in the
penthouses of expensive hotels sound like the rest of us riff-raff
doesn't it?). If you want to stick to 13R though look at how laundries
are treated in that document. What you describe is implied in the
fixture count tables in the annex where there is a distinction between
laundry facilities in each unit and common laundry facilities for the
purpose of determining water demand but not for occupancy definition.
As to how students live as opposed to the rest of us is not addressed
by ICC or NFPA. So far as life safety only systems go I vote for 13D,
two head calc and ten minute duration per the minimum standard allowed
by the building code. I see no fire protection advantage to the
four-head calc and longer duration of 13R but I do see the need for a
bigger tank and a listed pump which will be way more expensive.

On 10/23/07, Jay Stough <[EMAIL PROTECTED]> wrote:
> I would agree with you George.  In this case the most storage you will have
> in the basement is dirty laundry (28 days until Mom comes to do it for you)
> and cases of beer that might start appearing on Wednesday evening (and
> surprisingly disappear on Saturday evening).  Most people at that stage of
> their life are not filling the basement, like those of us that have lived in
> a house over 5 to 7 years.
>
> Joseph C. Stough SET, CFPS
> Tilley Fire Equipment Co.
> Tel. 215-345-8066 X22
> Fax: 215-345-9357
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] Behalf Of George
> Church
> Sent: Tuesday, October 23, 2007 6:00 AM
> To: [email protected]
> Subject: in or outside dwelling unit?
>
>
> Ok, I started my day by perusing the Archives, couldn't find the answer to
> this. See what I mean about not needing a life if you're in this business?
>
> Student housing in row homes.
> Each building is a single apt with 3 or 4 bedrooms, common kitchen, living
> and dining room, basement has laundry and an area to be used for storage.
> If you're a renter in this apartment, you have unrestricted access to the
> entire building, unless there's a tie on the doorknob.
>
> Due to unrelated students co-habitating, this falls under 13R (PA UCC is
> based on '03 IBC); if it were a single family living there, it'd be 13D.
> Stored water, #20 pump will be sole supply, central station.
>
> Any reason the basement would not be considered part of the Dwelling Unit?
> 13R definition includes common kitchen and sanitary facilities;
> wouldn't laundry count as part of sanitary facilities?
> Standard residential laundry W/D.
>
> The intent of 13R dwelling unit definition is obviously NOT to draw the line
> at a bedroom door; so if it isn't at the bedroom door, it'll include the
> halls, shared bathrooms, kitchen, LR/DR, and no wording remotely suggests
> the door in the kitchen that leads to the basement should be rated assembly
> or is a delineation between dwelling unit and "area outside dwelling unit".
>
> The basements contain 4 to 6 heads and flowing them all at .15 for tenant
> storage OH1 has a dramatic impact on pump and tank sizing, since rest of MRA
> is only 2 heads due to how cut-up the buildings are.
>
> It is NOT the same parameters as walking out of your apt in Sr Housing,
> taking the elevator to the basement, and entering the separate Tenant
> Storage with chicken wire cubicles. That's OH1 (since ceilings rarely exceed
> 8') Tenant Storage since the apt door is the line between inside and outside
> the dwelling unit.
>
> Anyone differ that the entire house is inside the dwelling unit?
>
> George Church
> Rowe Sprinkler
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....