But a storage (or non living space) basement is outside the dwelling unit in
a 13R situation. How is it different than the 12 lockers down the hall in
an traditional 13R application? There are properly rated doors and floors
between the basement or corridor and the traditional living spaces. Now the
proper rating might be 0 in your case and a bit more in a traditional 13R
apartment.
Your problem stems from the local amendment forcing 13R in what is elsewhere
13D. 13D doesn't have issues with areas outside the dwelling unit because
it's all the dwelling unit in a SFH. Granted with young kids and a wood
working shop in my basement it should be protected for plastics and OHII.
If you have areas outside the dwelling unit and you think you are using 13D
you probably have the wrong standard.
To slightly disagree with Roland the fact it is a basement used for
nonliving purposes (Den, bedrooms, etc) is irrelevant or not depending on
which standard you are using. The use is irrelevant in 13D but not in 13R or
13. Covering 6' of plastic in my basement with a .05 my not be good fire
protection but it is code complaint. Having a .05 in a little used basement
in a 13R may be adequate fire protection but it is not code complaint.
This is a case where logic should be left behind (as with some (but not all)
parts of the codes).
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Tuesday, October 23, 2007 9:38 AM
To: [email protected]
Subject: RE: in or outside dwelling unit?
Right now it is empty except for a washer and dryer- standard residential
models. Ceiling's about 8', so they can't pack it in.
And as you note, the fact that it is a basement is irrelevant, since I
believe the Dwelling unit includes the entire house.
If this was a large apt building, and there was no tenant storage area
outside the dwelling unit, then the 3 bedroom apt dwellers might all stick
their storage in the dining room. And no one would bat an eye if I covered
it with .005 any more than we would apply .15 OH1 to the utility room off
the kitchen, housing a craft area and W/D in any residential setting.
Unless I miss the point in 13R, if it is INSIDE THE DWELLING UNIT, it gets
covered under residential rules. If the heat pump was in the corner of that
utility room instead of a closet where any head covering 3'x5' would exceed
.15, there'd be no rated door to the kitchen, no OH1. Since there is no
distinction for basements within the dwelling unit definition, and no line
of demarcation explained, then why would the basement of a house that is one
three bedroom apt be considered OUTSIDE the dwelling unit?
Since I do not want to expose the educational institution to a lawsuit, I am
not attempting to stubstitute a 13d pump on steroids, we'll install a
#20-compliant pump. I believe a case for Equivalency exists with a paid FD
with several stations within 5~ 15 minute max response (awaiting FD
historical records data) and city hydrants, FDC, and voluntary sprinkler
system.
But I do NOT want to provide OH1 in an area INSIDE the dwelling unit since I
believe it defeats the intent of the Committee for an affordable life safety
system. If this was a commercial laundry like a hotel has, that'd be
completely different case. This is a home-style laundry.
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Tuesday, October 23, 2007 10:24 AM
To: [email protected]
Subject: Re: in or outside dwelling unit?
That fact that it is an basement is irrelevant. What is the area
used for, what is the fuel load like, and what is the ceiling?
Roland
On Oct 23, 2007, at 4:08 AM, Jay Stough wrote:
> I would agree with you George. In this case the most storage you
> will have
> in the basement is dirty laundry (28 days until Mom comes to do it
> for you)
> and cases of beer that might start appearing on Wednesday evening (and
> surprisingly disappear on Saturday evening). Most people at that
> stage of
> their life are not filling the basement, like those of us that have
> lived in
> a house over 5 to 7 years.
>
> Joseph C. Stough SET, CFPS
> Tilley Fire Equipment Co.
> Tel. 215-345-8066 X22
> Fax: 215-345-9357
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)