George,

I think you may be trying to apply the requirements in 13R for garages
to basements. This basement would just be like storage lockers or it
could be considered a subterranean laundry room. What would put it
outside the dwelling unit? Dwelling and dwelling unit have distinctive
definitions in IBC. you may want to look in your PA modified version
in case they altered them. I still think that this is a 13D by IBC,
Chapter Three "Occupancies" leading to NFPA 13D as the applicable fire
sprinkler standard. This is the case whether voluntary or required. I
had to do some teaching so this is coming later in the thread than
intended.

On 10/23/07, George Church <[EMAIL PROTECTED]> wrote:
> I won't argue that if I were chief, I would allow a voluntary 13D in a
> heartbeat. However, I believe I am still required to provide a 13R, we have
> a modified '06 IBC here in PA. For sake of my question, assume it IS 13R:
>
> Does the dwelling unit in a one apartment building with unrestricted access
> to the entire building mean the basement is part of the dwelling unit?
>
> If not, where (and how) is the line drawn between inside and outside the
> dwelling unit if the basement is deemed "outside the dwelling unit" ?
>
> While the definition of Dwelling Unit in #13R is descriptive, it would be
> helpful to have a definition of "Areas Outside of Dwelling Units" with what
> criteria should be used to judge what is Outside the Dwelling Unit.
>
> glc
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
> Sent: Tuesday, October 23, 2007 10:13 AM
> To: [email protected]
> Subject: Re: in or outside dwelling unit?
>
> George,
>
> I think you have a 13D. IBC 2006 (out West we're progressive so we
> burnt our 2003s) R-2 is for, "...apartment houses, boarding houses
> (non-transient)...dormitories, fraternities...monasteries...." Your's
> is obviously one of these but there's a caveat, "Congregate living
> facilities with 16 or fewer occupants are permitted to comply with the
> construction requirements for group R-3." R-3 is for, among other
> things, "Congregate living facilities with 16 or fewer persons." R3 is
> also for, "Buildings that do not contain more than two dwelling
> units." You are a 13D. As important as what you is is what you ain't
> and you ain't an R-1 which are essentially sleeping quarters for
> transients (makes those rich folks that live year round in the
> penthouses of expensive hotels sound like the rest of us riff-raff
> doesn't it?). If you want to stick to 13R though look at how laundries
> are treated in that document. What you describe is implied in the
> fixture count tables in the annex where there is a distinction between
> laundry facilities in each unit and common laundry facilities for the
> purpose of determining water demand but not for occupancy definition.
> As to how students live as opposed to the rest of us is not addressed
> by ICC or NFPA. So far as life safety only systems go I vote for 13D,
> two head calc and ten minute duration per the minimum standard allowed
> by the building code. I see no fire protection advantage to the
> four-head calc and longer duration of 13R but I do see the need for a
> bigger tank and a listed pump which will be way more expensive.
>
> On 10/23/07, Jay Stough <[EMAIL PROTECTED]> wrote:
> > I would agree with you George.  In this case the most storage you will
> have
> > in the basement is dirty laundry (28 days until Mom comes to do it for
> you)
> > and cases of beer that might start appearing on Wednesday evening (and
> > surprisingly disappear on Saturday evening).  Most people at that stage of
> > their life are not filling the basement, like those of us that have lived
> in
> > a house over 5 to 7 years.
> >
> > Joseph C. Stough SET, CFPS
> > Tilley Fire Equipment Co.
> > Tel. 215-345-8066 X22
> > Fax: 215-345-9357
> > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
> >
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] Behalf Of George
> > Church
> > Sent: Tuesday, October 23, 2007 6:00 AM
> > To: [email protected]
> > Subject: in or outside dwelling unit?
> >
> >
> > Ok, I started my day by perusing the Archives, couldn't find the answer to
> > this. See what I mean about not needing a life if you're in this business?
> >
> > Student housing in row homes.
> > Each building is a single apt with 3 or 4 bedrooms, common kitchen, living
> > and dining room, basement has laundry and an area to be used for storage.
> > If you're a renter in this apartment, you have unrestricted access to the
> > entire building, unless there's a tie on the doorknob.
> >
> > Due to unrelated students co-habitating, this falls under 13R (PA UCC is
> > based on '03 IBC); if it were a single family living there, it'd be 13D.
> > Stored water, #20 pump will be sole supply, central station.
> >
> > Any reason the basement would not be considered part of the Dwelling Unit?
> > 13R definition includes common kitchen and sanitary facilities;
> > wouldn't laundry count as part of sanitary facilities?
> > Standard residential laundry W/D.
> >
> > The intent of 13R dwelling unit definition is obviously NOT to draw the
> line
> > at a bedroom door; so if it isn't at the bedroom door, it'll include the
> > halls, shared bathrooms, kitchen, LR/DR, and no wording remotely suggests
> > the door in the kitchen that leads to the basement should be rated
> assembly
> > or is a delineation between dwelling unit and "area outside dwelling
> unit".
> >
> > The basements contain 4 to 6 heads and flowing them all at .15 for tenant
> > storage OH1 has a dramatic impact on pump and tank sizing, since rest of
> MRA
> > is only 2 heads due to how cut-up the buildings are.
> >
> > It is NOT the same parameters as walking out of your apt in Sr Housing,
> > taking the elevator to the basement, and entering the separate Tenant
> > Storage with chicken wire cubicles. That's OH1 (since ceilings rarely
> exceed
> > 8') Tenant Storage since the apt door is the line between inside and
> outside
> > the dwelling unit.
> >
> > Anyone differ that the entire house is inside the dwelling unit?
> >
> > George Church
> > Rowe Sprinkler
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to