Interesting: The cut sheet on the sprinkler has the following in it: When properly installed, there is a nominal 3/32 inch (2,4 mm) air gap between the lip of the Cover Plate and the ceiling, as shown in Figure 2. This air gap is necessary for proper operation of the sprinkler.
They then go on to seal this gap with the air and dust seal. I was under the impression that the gap was critical for the proper operation of the sprinkler, but this doesn't seem to be the case. This same condition exists for the Reliable. Can someone explain why this gap is not required when the seal is applied, but is required otherwise. Thanks Pete VA -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Richard Mote Sent: Tuesday, October 30, 2007 11:41 AM To: [email protected] Subject: Re: Clean room sprinkler heads w/ covers or here http://www.tyco-fireproducts.com/TD_TFP/TFP/TFP181_07_2004.pdf R. Mote ----- Original Message ----- From: "Tambini, Ed" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Tuesday, October 30, 2007 9:43 AM Subject: RE: Clean room sprinkler heads w/ covers try here: http://www.reliablesprinkler.com/pdfs/products/123%20G4%20G4FR%20Sealing %20Concealed.pdf ed aero -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ford, Charles Sent: Tuesday, October 30, 2007 6:31 AM To: [email protected] Subject: RE:Clean room sprinkler heads w/ covers A customer is asking us to provide sprinklers for a clean room. We saw some installed ones and they appear to have very large cover plates that are rubber gasketed at the ceiling. Manufacturer unknown. Anybody run into these and knows their origin? Burton Ford SET, CFPS Member AFAA [EMAIL PROTECTED] 267-487-1000 Fax 267-487-1010 This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. Thank you. Cintas Corporation This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)