The overriding concern is for cleanliness, in a HEPA filtered clean
room/operating room environment.
The application requirements for preventing foreign materials outweigh the
requirement for QR, IMHO.

The gap is for prewarming of the fusible link/glass bulb

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Wednesday, October 31, 2007 2:22 PM
To: [email protected]
Subject: RE: Clean room sprinkler heads w/ covers

It doesn't answer your question, but I noticed that for a least one of the
manufacturers, if the air/dust seal is used, the sprinkler is no longer
quick response.  A bit of an issue in light hazard occupancies.

Ed Kramer
Littleton, CO


>Interesting:  The cut sheet on the sprinkler has the following in it:
>
>When properly installed, there is a
>nominal 3/32 inch (2,4 mm) air gap
>between the lip of the Cover Plate and
>the ceiling, as shown in Figure 2. This
>air gap is necessary for proper operation
>of the sprinkler.
>
>They then go on to seal this gap with the air and dust seal.
>
>I was under the impression that the gap was critical for the proper
>operation of the sprinkler, but this doesn't seem to be the case.  This
>same condition exists for the Reliable.
>
>Can someone explain why this gap is not required when the seal is
>applied, but is required otherwise.
>
>Thanks
>
>Pete
>VA


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to