The gap between the cover plate and the skirt does contribute to preheating the 
thermal element prior to the cover plate falling off.  Even with the gap 
covered with the gasket, however, the operation of the sprinkler still falls 
within the standard response time criteria when subjected to room heat 
sensitivity testing.  Therefore, the gasket is listed with the sprinkler, 
whereas varying thicknesses of any type of caulk sealant used by an installer 
or building owner to seal the gap is not.
 
Regards,
 
Salvatore J. Izzo, P.E.
Manager - Reliable Technical Services

________________________________

From: [EMAIL PROTECTED] on behalf of Ed Kramer
Sent: Wed 10/31/2007 14:22
To: [email protected]
Subject: RE: Clean room sprinkler heads w/ covers



It doesn't answer your question, but I noticed that for a least one of the
manufacturers, if the air/dust seal is used, the sprinkler is no longer
quick response.  A bit of an issue in light hazard occupancies.

Ed Kramer
Littleton, CO


>Interesting:  The cut sheet on the sprinkler has the following in it:
>
>When properly installed, there is a
>nominal 3/32 inch (2,4 mm) air gap
>between the lip of the Cover Plate and
>the ceiling, as shown in Figure 2. This
>air gap is necessary for proper operation
>of the sprinkler.
>
>They then go on to seal this gap with the air and dust seal.
>
>I was under the impression that the gap was critical for the proper
>operation of the sprinkler, but this doesn't seem to be the case.  This
>same condition exists for the Reliable.
>
>Can someone explain why this gap is not required when the seal is
>applied, but is required otherwise.
>
>Thanks
>
>Pete
>VA


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to