Why not use a pendent and seal the hole above the fusible element?  Is
the pendent a problem in the clean room such that you need the flat
cover plate? 

Pete

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Wednesday, October 31, 2007 3:32 PM
To: [email protected]
Subject: Re: Clean room sprinkler heads w/ covers

Actually many of these applications are such that were this option not 
available they would opt. to leave out protection, or have to install an

expensive alternative system. This choice is usually made by the 
Arch/owner's rep. not the Sprinkler guy.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Ed Kramer" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, October 31, 2007 2:03 PM
Subject: RE: Clean room sprinkler heads w/ covers


>I agree, George.  And as long as owner, AHJ, insurance interests, judge
&
> jury agree, there is no issue.
>
> Ed Kramer
> Littleton, CO
>
>
>>The overriding concern is for cleanliness, in a HEPA filtered clean
>>room/operating room environment.
>>The application requirements for preventing foreign materials outweigh
the
>>requirement for QR, IMHO.
>>
>>The gap is for prewarming of the fusible link/glass bulb
>>
>>glc
>>
>>-----Original Message-----
>>From: [EMAIL PROTECTED]
>>[mailto:[EMAIL PROTECTED] On Behalf Of Ed
Kramer
>>Sent: Wednesday, October 31, 2007 2:22 PM
>>To: [email protected]
>>Subject: RE: Clean room sprinkler heads w/ covers
>>
>>It doesn't answer your question, but I noticed that for a least one of
the
>>manufacturers, if the air/dust seal is used, the sprinkler is no
longer
>>quick response.  A bit of an issue in light hazard occupancies.
>>
>>Ed Kramer
>>Littleton, CO
>>
>>
>>>Interesting:  The cut sheet on the sprinkler has the following in it:
>>>
>>>When properly installed, there is a
>>>nominal 3/32 inch (2,4 mm) air gap
>>>between the lip of the Cover Plate and
>>>the ceiling, as shown in Figure 2. This
>>>air gap is necessary for proper operation
>>>of the sprinkler.
>>>
>>>They then go on to seal this gap with the air and dust seal.
>>>
>>>I was under the impression that the gap was critical for the proper
>>>operation of the sprinkler, but this doesn't seem to be the case.
This
>>>same condition exists for the Reliable.
>>>
>>>Can someone explain why this gap is not required when the seal is
>>>applied, but is required otherwise.
>>>
>>>Thanks
>>>
>>>Pete
>>>VA
>>
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to