We finished our glycerin conversion this past week.  All went fine with the
exception of the expansion tank.  I had some trouble getting it to hold 70
PSI (70-75 street pressure).  I pumped it with an air compressor before we
filled and checked it after we had the glycerin to 75 PSI, it fell to 60
PSI.  Strange.
I topped it off again and it seemed fine but I'm tempted to head down and
check it again.  We put in five low point drains per 25-2008 as it had 340
gallons of glycerin in it.
We also cut 1/2" plugged ball valves at the tops of all the risers (25 of
them) to purge and vent.  I was surprised at how much air we got out once it
was up to pressure, glad I did that.  I wondered if I was eliminating some
additional expansion but once we opened the water valve, we got a little
gurgle of water past the check and that was it.  Hopefully just a little
water sneaked bye, we pumped it to 5 psi above static pressure too.  I
suggested the owner save the glycerin drums a if they ever had to make any
changes, they'd have to dump all that glycerin.  I made signs on my plotter
in vinyl for the low points, fill and drain locations and also a big one
stating the system had glycerin in it and took the handle off the end of
line and put a sign on that too.
Tom


Hello Tom,

The instructions with the one I have say 2 PSI under or over (I forgot
which) system pressure, I will look Monday and email. Check the local Fire
Extinguisher recharge co. for Nitrogen, They use in in Dry Chemical
extinguishers. The one I have has a regular valve stem on it like a tire.
Fills with the same adapter as a tire (Same as the one that used to be on
Badger Brand Water Extinguishers).