I can´t find your numbers.
I think what you are referring to is:  2007 NFPA 13, Table 17.2.3.1
but for uncartoned (exposed) unexpanded,
the pressures and K-factors do not match
your quotations at the 25 ft storage height.

the pressures and K-factors come close to
matching -- for cartoned unexpanded, at
25 ft storage under 30 ft building height,
but I see the K25 at 15psig, not 25 P psig.

the pattern with the latter is one that i remarked on
roughly 2 years ago, and got lambasted
for not knowing what I was talking about.
But the table remains the same, only my
grey matter has degenerated in that time frame.

regardless of the pressure, about the same amount
of water is being delivered.  within 5% for this instance.
as noted then, and repeated again, it seems that the criticality
is not so much in the momentum of the sprinkler water
forcing its way down through the fire plume, as it is in
achieving a critical amount of water onto the fire.
Certainly, we are past the point where a critical
pressure is reached whereby the fire plume can no
longer put up even a sham of resistance
to the onslaught of water drafted through the
ESFR´s.

What seems critical is:  the amount of water thrown
onto the fire, and getting that water on the fire FAST....
hence the incorporation of low RTI´s into the ESFR´s.


scot deal
excelsior fire



> Anyone have a theory why uncartoned unexpanded plastics doesn't follow the
> pressure patterns of everything else. In all other cases outside this the
> smaller the orifice the larger the pressure.
>