I can´t find your numbers. I think what you are referring to is: 2007 NFPA 13, Table 17.2.3.1 but for uncartoned (exposed) unexpanded, the pressures and K-factors do not match your quotations at the 25 ft storage height.
the pressures and K-factors come close to matching -- for cartoned unexpanded, at 25 ft storage under 30 ft building height, but I see the K25 at 15psig, not 25 P psig. the pattern with the latter is one that i remarked on roughly 2 years ago, and got lambasted for not knowing what I was talking about. But the table remains the same, only my grey matter has degenerated in that time frame. regardless of the pressure, about the same amount of water is being delivered. within 5% for this instance. as noted then, and repeated again, it seems that the criticality is not so much in the momentum of the sprinkler water forcing its way down through the fire plume, as it is in achieving a critical amount of water onto the fire. Certainly, we are past the point where a critical pressure is reached whereby the fire plume can no longer put up even a sham of resistance to the onslaught of water drafted through the ESFR´s. What seems critical is: the amount of water thrown onto the fire, and getting that water on the fire FAST.... hence the incorporation of low RTI´s into the ESFR´s. scot deal excelsior fire > Anyone have a theory why uncartoned unexpanded plastics doesn't follow the > pressure patterns of everything else. In all other cases outside this the > smaller the orifice the larger the pressure. > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)