Joe- These words, and the time bombs we can plant while being "right" or "compliant" should be required to be memorized by large groups of us; including ourselves as contractors, your insurance side of the house, AHJ/Inspectors, and PE's who assume anything specified to less than 3 decimal places is a guess.
Thanks again for your insight. George Church Rowe Sprinkler -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins Sent: Monday, December 10, 2007 12:18 PM To: [email protected] Subject: Re: ESFR Pressure Anomaly <Snip> Anytime you treat NFPA 13 as a scientific, consistent engineering document, you're asking for trouble! It's a large collection of loosely connected fire protection rules that range from well-supported to unsupported, depending on when and under what circumstances they were adopted. That doesn't make it a bad standard to follow, but it does make it impossible to read between the lines without risking faulty conclusions on occasion. <Snip: Area Density Curve Example, good as it is, to allow us to jump right to the conclusion> Those designers who play the game of sliding up the curve to sneak by with 130 sq.ft. spacing and/or K5.6 sprinklers to save a few pennies do so at the cost of fire protection that is on the ragged edge, even though 13 can be interpreted to say that any point on the curve with any sprinkler and any spacing will provide the same protection. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)