Joe-

These words, and the time bombs we can plant while being "right" or
"compliant" should be required to be memorized by large groups of us;
including ourselves as contractors, your insurance side of the house,
AHJ/Inspectors, and PE's who assume anything specified to less than 3
decimal places is a guess.

Thanks again for your insight.

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
Sent: Monday, December 10, 2007 12:18 PM
To: [email protected]
Subject: Re: ESFR Pressure Anomaly

<Snip>

Anytime you treat NFPA 13 as a scientific, consistent engineering 
document, you're asking for trouble!  It's a large collection of loosely 
connected  fire protection rules that range from well-supported to 
unsupported, depending on when and under what circumstances they were 
adopted.  That doesn't make it a bad standard to follow, but it does 
make it impossible to read between the lines without risking faulty 
conclusions on occasion.

<Snip: Area Density Curve Example, good as it is, to allow us to jump right
to the conclusion>

Those designers who play the game of sliding up the curve to sneak by 
with 130 sq.ft. spacing and/or K5.6 sprinklers to save a few pennies do 
so at the cost of fire protection that is on the ragged edge, even 
though 13 can be interpreted to say that any point on the curve with any 
sprinkler and any spacing will provide the same protection.