I was reading from the cut sheet, technically FM criteria. NFPA according to the cut sheet there is no protection scheme for the K25. Even in the table you reference there is no ESFR 25 for this.
As far as flows 25's = 178gpm, 17's = 99.4pgm and 14's 99 gpm. So I can go along with the meaningless gpm on the 14's vs. 17's but not on the 25's. Joe wrote: "Anytime you treat NFPA 13 as a scientific, consistent engineering document, you're asking for trouble!" I did make that mistake apparently. Suckered right in on a Monday morning when I normally should know better. So the real answer is it was tested at 50 with no implied meaning. I have seen James Golinveaux (Tyco) SFPE's presentation on area/density curves - which is what really got me into trouble thinking too much on the anomaly. If you (anyone in this business) haven't seen it you really should. Especially, the younger you are and not having the opportunity to live professionally though the evolution. And when you see it don't necessarily apply it to ESFR and special testing schemes like I mistakenly did. Chris -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... .... Sent: Monday, December 10, 2007 11:09 AM To: [email protected] Subject: ESFR Pressure Anomaly I can´t find your numbers. I think what you are referring to is: 2007 NFPA 13, Table 17.2.3.1 but for uncartoned (exposed) unexpanded, the pressures and K-factors do not match your quotations at the 25 ft storage height. the pressures and K-factors come close to matching -- for cartoned unexpanded, at 25 ft storage under 30 ft building height, but I see the K25 at 15psig, not 25 P psig. the pattern with the latter is one that i remarked on roughly 2 years ago, and got lambasted for not knowing what I was talking about. But the table remains the same, only my grey matter has degenerated in that time frame. regardless of the pressure, about the same amount of water is being delivered. within 5% for this instance. as noted then, and repeated again, it seems that the criticality is not so much in the momentum of the sprinkler water forcing its way down through the fire plume, as it is in achieving a critical amount of water onto the fire. Certainly, we are past the point where a critical pressure is reached whereby the fire plume can no longer put up even a sham of resistance to the onslaught of water drafted through the ESFR´s. What seems critical is: the amount of water thrown onto the fire, and getting that water on the fire FAST.... hence the incorporation of low RTI´s into the ESFR´s. scot deal excelsior fire > Anyone have a theory why uncartoned unexpanded plastics doesn't follow the > pressure patterns of everything else. In all other cases outside this the > smaller the orifice the larger the pressure. > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)