Table 17.2.3.1 DOES reference the K25 for your case, uncartoned (exposed) unexpanded plastic. look at 25 ft storage (your specification) at 40 ft storage height. (per my reference). The flows in that NFPA row goes as you shows below.
I think the reason the K25 is required to thrown down so much more water than the K17 and the K14 at this configuration of heights is for the same reason that Joe mentioned. The K25 was the first kid on the block to test out. As such, they wanted to make sure they would pass. the other heads had the benefit of the first guys experience, and skinnied down the safety margin (to the hairy edge). So it would SEEM there IS some safety with the K25 in this configuration of building height and storage height. I am willing to bet, if they took the K25 and tested it at the 100 gpm the others throw down with, that it would pass the test at close to 100 gmp, too. of course, this is monday morning quarterbacking. i prefer to use my gut instinct, more than 3 decimal points. this seems like deja vú from 2 years ago, too. ;- ) scot deal excelsior fire engineering On 12/10/07, Chris Cahill <[EMAIL PROTECTED]> wrote: > > I was reading from the cut sheet, technically FM criteria. NFPA according > to the cut sheet there is no protection scheme for the K25. Even in the > table you reference there is no ESFR 25 for this. > > As far as flows 25's = 178gpm, 17's = 99.4pgm and 14's 99 gpm. So I can > go > along with the meaningless gpm on the 14's vs. 17's but not on the 25's. > > > Joe wrote: > "Anytime you treat NFPA 13 as a scientific, consistent engineering > document, > you're asking for trouble!" > > I did make that mistake apparently. Suckered right in on a Monday morning > when I normally should know better. > > So the real answer is it was tested at 50 with no implied meaning. > > I have seen James Golinveaux (Tyco) SFPE's presentation on area/density > curves - which is what really got me into trouble thinking too much on the > anomaly. If you (anyone in this business) haven't seen it you really > should. Especially, the younger you are and not having the opportunity to > live professionally though the evolution. And when you see it don't > necessarily apply it to ESFR and special testing schemes like I mistakenly > did. > > Chris > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of å... .... > Sent: Monday, December 10, 2007 11:09 AM > To: [email protected] > Subject: ESFR Pressure Anomaly > > I can´t find your numbers. > I think what you are referring to is: 2007 NFPA 13, Table 17.2.3.1 > but for uncartoned (exposed) unexpanded, > the pressures and K-factors do not match > your quotations at the 25 ft storage height. > > the pressures and K-factors come close to > matching -- for cartoned unexpanded, at > 25 ft storage under 30 ft building height, > but I see the K25 at 15psig, not 25 P psig. > > the pattern with the latter is one that i remarked on > roughly 2 years ago, and got lambasted > for not knowing what I was talking about. > But the table remains the same, only my > grey matter has degenerated in that time frame. > > regardless of the pressure, about the same amount > of water is being delivered. within 5% for this instance. > as noted then, and repeated again, it seems that the criticality > is not so much in the momentum of the sprinkler water > forcing its way down through the fire plume, as it is in > achieving a critical amount of water onto the fire. > Certainly, we are past the point where a critical > pressure is reached whereby the fire plume can no > longer put up even a sham of resistance > to the onslaught of water drafted through the > ESFR´s. > > What seems critical is: the amount of water thrown > onto the fire, and getting that water on the fire FAST.... > hence the incorporation of low RTI´s into the ESFR´s. > > > scot deal > excelsior fire > > > > > Anyone have a theory why uncartoned unexpanded plastics doesn't follow > the > > pressure patterns of everything else. In all other cases outside this > the > > smaller the orifice the larger the pressure. > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)