OIC.

Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan Peterson
Sent: Wednesday, January 02, 2008 3:07 PM
To: [email protected]
Subject: RE: Hanger Size Question

The reason for using larger hangers is for hangers on CPVC pipe.
Shooting CPVC pipe to a concrete deck using 2-hole straps causes the pipe to
deflect because of the larger outside diameter of the fittings.
This deflection is causing, or adding to other causes of, Environmental
Stress Cracking. Using a strap one size larger than the CPVC pipe prevents
this deflection.

Ryan Peterson
Wayne Automatic Fire Sprinklers, Inc.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Wednesday, January 02, 2008 2:56 PM
To: [email protected]
Subject: RE: Hanger Size Question

Why would you want to do that? I would use a 1" hanger for 1" pipe,  1 1/4"
hanger for 1 1/4", etc.


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan Peterson
Sent: Wednesday, January 02, 2008 1:43 PM
To: [email protected]
Subject: RE: Hanger Size Question

2002, but 9.1.1.6 governs trapeze and I'm more concerned with general hanger
size; such as, hanging 1" pipe with an 1 1/4" 2-hole strap.

Ryan Peterson
Wayne Automatic Fire Sprinklers, Inc.
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew
Walsvik
Sent: Wednesday, January 02, 2008 11:39 AM
To: [email protected]
Subject: RE: Hanger Size Question

Are you using NFPA 13 2002? Or 2007?

The requirements of 9.1.1.6 were changed in the 2007 edition.

Matthew D. Walsvik, EIT
Civil/Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Ave. S.
Fargo, ND 58106/9615

Phone: 701.280.8700
Direct: 701.280.8694
Fax:      701.280.8739

[EMAIL PROTECTED]
www.ulteig.com

Confidentiality Notice

This message may contain privileged and confidential information. If you
think, for any reason, this message may have been addressed to you in error,
you must not disseminate copy or take any action in reliance on it, and we
would ask you to notify me immediately by return email to
[EMAIL PROTECTED] 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan Peterson
Sent: Wednesday, January 02, 2008 9:44 AM
To: [email protected]
Subject: Hanger Size Question

I thought I read that it was acceptable to install pipe using a hanger one
pipe size larger than the pipe being installed but I can't seem to find it.
Can someone remind me where I would have read it?
 
Thanks,
 
Ryan Peterson
Wayne Automatic Fire Sprinklers, Inc.
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]