Your concern is valid. The 1-1/4" strap is not listed for service on 1" pipe. 
UL tests the 1-1/4" strap with 1-1/4" pipe, not 1".
   
  Scott Mitchell 

Ryan Peterson <[EMAIL PROTECTED]> wrote:
  2002, but 9.1.1.6 governs trapeze and I'm more concerned with general
hanger size; such as, hanging 1" pipe with an 1 1/4" 2-hole strap.

Ryan Peterson
Wayne Automatic Fire Sprinklers, Inc.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew
Walsvik
Sent: Wednesday, January 02, 2008 11:39 AM
To: [email protected]
Subject: RE: Hanger Size Question

Are you using NFPA 13 2002? Or 2007?

The requirements of 9.1.1.6 were changed in the 2007 edition.

Matthew D. Walsvik, EIT
Civil/Fire Protection Engineer
Ulteig Engineers, Inc.
3350 38th Ave. S.
Fargo, ND 58106/9615

Phone: 701.280.8700
Direct: 701.280.8694
Fax: 701.280.8739

[EMAIL PROTECTED]
www.ulteig.com

Confidentiality Notice

This message may contain privileged and confidential information. If you
think, for any reason, this message may have been addressed to you in
error, you must not disseminate copy or take any action in reliance on
it, and we would ask you to notify me immediately by return email to
[EMAIL PROTECTED] 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan
Peterson
Sent: Wednesday, January 02, 2008 9:44 AM
To: [email protected]
Subject: Hanger Size Question

I thought I read that it was acceptable to install pipe using a hanger
one pipe size larger than the pipe being installed but I can't seem to
find it. Can someone remind me where I would have read it?

Thanks,

Ryan Peterson
Wayne Automatic Fire Sprinklers, Inc.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Be a better friend, newshound, and know-it-all with Yahoo! Mobile.  Try it now.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to