Is the occupancy light hazard?
Are there any other combustibles besides the roof construction?.
Can significant other materials be stored or used here?
Will the tank cause sprinkler flow obstructions?
Is the tank filled with water?

If you can answer these Q's you will have the answer.

Art

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Friday, January 04, 2008 7:25 AM
To: [email protected]
Subject: another Attic Sprinkler question

I am designing a system for the top level of a tower (the same one 
from a previous post). The space is roughly 25 x 25. The height at 
the hip is 22 feet and at the peak of the roof is about 30 ft. The 
peak is in the geometric center and there are 4 sloped surfaces, 
similar to the top of the Washington Monument. The space is almost 
completely filled by an empty, open-topped steel tank about 20 ft 
high. There are existing sprinklers at the roof, but the piping is in 
bad shape and needs to be replaced. I designed a system using 7 
regular sprinklers. The contractor who has to do the job has asked if 
the Tyco Attic Hip sprinklers could be used in this situation. My 
immediate reaction was no because I don't think this qualifies under 
the definition of an attic. However, I thought I would put it out to 
see if anyone has used them in this type of situation.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to