So how about showing the AHJ the listings for the K14's and the listing for those being used. "Yes sir, where there are height restrictions for sprinklers like those K 14's it is shown in the listing. There are no such restrictions on the ones we are using." Ed
Joe Hankins <[EMAIL PROTECTED]> wrote: Sprinklers aren't "rated" for building height in and of themselves, as the maximum height it depends on a lot of factors. So long as the sprinklers are listed for the NFPA 13 design you are using, that's all you need. For example, K14 ESFRs are limited to 32 ft. buildings at 50 psi, but can go to 40 ft. at 75 psi. Joe Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)