So how about showing the AHJ the listings for the K14's and the listing for 
those being used.  
   
  "Yes sir, where there are height restrictions for sprinklers like those K 
14's it is shown in the listing.  There are no such restrictions on the ones we 
are using."
   
  Ed

Joe Hankins <[EMAIL PROTECTED]> wrote:
  Sprinklers aren't "rated" for building height in and of themselves, as 
the maximum height it depends on a lot of factors. So long as the 
sprinklers are listed for the NFPA 13 design you are using, that's all 
you need. For example, K14 ESFRs are limited to 32 ft. buildings at 50 
psi, but can go to 40 ft. at 75 psi.

Joe