There is technically no limit on the height at which most sprinklers can be utilized. The more usual situation is when a specific sprinkler has a specific listing limiting its usage to a certain height.
The number your memory is serving to you comes from the Life Safety Code and references a height of 55ft. However, it doesn't LIMIT you by the standard. It only directs you to give consideration to the fact that the height may cause a delay in the sprinkler activation. The considerations may be to increase your design area, design density, or both to more reliably control a fire in areas where the ceiling is at more extreme heights. Thanks, Ray Vance Wyane Automatic Fire Sprinklers,'Inc. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, January 29, 2008 9:43 AM To: [email protected] Subject: Max Ceiling Heights Forum, I just got back some comments from the local AHJ on a project we are doing and he's asking me to verify that the heads we are using are rated for ceilings over 30'. I've spoke with the manufacturer and he said he doesn't have anything on min./max. ceiling heights. If memory serves me isn't 50' somewhere in NFPA? Any help would be appreciated. Regards, <http://www.firstdefensefire.com/> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)