There is technically no limit on the height at which most sprinklers can
be utilized.
The more usual situation is when a specific sprinkler has a specific
listing limiting its usage to a certain height.

The number your memory is serving to you comes from the Life Safety Code
and references a height of 55ft.

However, it doesn't LIMIT you by the standard. It only directs you to
give consideration to the fact that the height may cause a delay in the
sprinkler activation.
The considerations may be to increase your design area, design density,
or both to more reliably control a fire in areas where the ceiling is at
more extreme heights.

Thanks,

Ray Vance
Wyane Automatic Fire Sprinklers,'Inc. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, January 29, 2008 9:43 AM
To: [email protected]
Subject: Max Ceiling Heights

Forum,
I just got back some comments from the local AHJ on a project we are
doing and he's asking me to verify that the heads we are using are rated
for ceilings over 30'. I've spoke with the manufacturer and he said he
doesn't have anything on min./max. ceiling heights. If memory serves me
isn't 50'
somewhere in NFPA? Any help would be appreciated.
 

Regards,

  <http://www.firstdefensefire.com/> 

 

 