What we deal with here in Las Vegas are the local amendments to the
codes and NFPA 13.  When a ceiling height is between 25 and 50 feet
above the floor below quick-response sprinklers with a minimum K-factor
of 11.2 is required.  Once a ceiling height exceeds 50 feet a fire
protection engineer has to meet with the AHJ to discuss the hazards
associated, expected fire size to activate closed head sprinklers, etc.
The expected fire size to activate the sprinklers at a certain height
may be too large for comfort and deluge systems are proposed.  
 
 
Carl Chappell
Las Vegas, NV 89109
Phone: (702) 699-5391
Fax: (702) 699-5534
Cell: (702) 400-8736


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, January 29, 2008 7:02 AM
To: [email protected]
Subject: RE: Max Ceiling Heights

Certain types of sprinklers have specific limitations and they are
usually listed as such, typically those designated for storage
occupancies.  Most Control Mode sprinklers don't list any restrictions
and so far I haven't been able to find anything in NFPA stating an NFPA
imposed restriction.  NFPA defers to the mfgr data for installation
issues.

Dealt with this issue ad naseum on a 100ft high structure.   I contacted
one of the Sprinkler mfgrs and they were very helpful in explaining that
in my case even at 100ft the sprinklers will operate.  The fire does
have to be large enough to bring the ceiling temps up to the release
temps of the heads and that could take a little longer than in a 20-30ft
high bldg and might trigger more heads.  

If the AHJ is being persistent, ask the mfgr to write a letter
explaining the operation of the heads at the higher elevation will occur
and whatever other blah, blah blah words they need.  

Just something to satisfy the AHJ.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, January 29, 2008 9:43 AM
To: [email protected]
Subject: Max Ceiling Heights

Forum,
I just got back some comments from the local AHJ on a project we are
doing and he's asking me to verify that the heads we are using are rated
for ceilings over 30'. I've spoke with the manufacturer and he said he
doesn't have anything on min./max. ceiling heights. If memory serves me
isn't 50'
somewhere in NFPA? Any help would be appreciated.
 

Regards,

  <http://www.firstdefensefire.com/> 

 

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to