Can you cover the room with a single sidewall sprinkler installed flush with
the bottom of the soffits/bulkheads? Use a residential sprinkler listed for
upto 12 inches below the ceiling. The flow for the 0.1 density might still
be greater than the listed flow for 12 inches below the ceiling.

Tony  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: January 29, 2008 5:04 AM
To: [email protected]
Subject: 13 residential obstructions

I am working on a modification to an existing system in a residential
occupancy. The design basis for the system is NFPA 13 (2002) Section
11.2.3.5 (4 residential sprinkelrs, 0.10 density). In the revision, the
architect has added soffits and drop ceiling areas in certain rooms. As an
example, in the bathroom (>54 sqft), there are two areas where the ceiling
is 1 ft lower than the rest of the space, and greater than 30" from the
wall. Due to the size of the room, the distance required for obstructions
against a wall cannot be met. 
Section 8-10, which covers installation of residential sprinklers, does not
incorporate the same criteria for ceiling pockets as the sections for
commercial sprinklers. This being the case, the bathroom will require 3
sprinklers instead of 1 if the soffits are not there. 
The entire room is 90 square feet. Three sprinklers does seem like overkill.
We could switch to a commercial quick response sprinkler for this space, but
I do not necessarily want to mix residential and commercial within a unit.
It could create problems down the road for maintenance. This project has
enough of a sordid history. Any thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to