This thread reminds me of a dilemma I tussled with last week. In regards to residential sidewalls, section 8.10.7.1.2 (02) says not to install residential sidewalls within 8' of a light "or similar obstructions." It doesn't provide any exceptions, such as the light being only 4" deep and the sidewall installed 6" down from the ceiling. It simply says you can't do it.
Is a soffit along the wall opposite the sidewall considered a "similar obstruction"? I have a project where a 24" deep soffit is installed along 1 wall of the bedroom and along 1 wall of the living area (for ductwork). Disregarding the soffits, sidewalls would work wonderfully. If I consider the soffit a "similar obstruction", that pretty much eliminates the use of sidewalls. Am I missing something? Am I misinterpreting the intent of 8.10.7.1.2? Ed Kramer Littleton, CO _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)