This thread reminds me of a dilemma I tussled with last week.  In regards to
residential sidewalls, section 8.10.7.1.2 (02) says not to install
residential sidewalls within 8' of a light "or similar obstructions."  It
doesn't provide any exceptions, such as the light being only 4" deep and the
sidewall installed 6" down from the ceiling.  It simply says you can't do
it.  

Is a soffit along the wall opposite the sidewall considered a "similar
obstruction"?  I have a project where a 24" deep soffit is installed along 1
wall of the bedroom and along 1 wall of the living area (for ductwork).
Disregarding the soffits, sidewalls would work wonderfully.  If I consider
the soffit a "similar obstruction", that pretty much eliminates the use of
sidewalls.  Am I missing something?  Am I misinterpreting the intent of
8.10.7.1.2?

Ed Kramer
Littleton, CO