Thank you, Tony.  I didn't remember this being discussed on the forum, so
I'll review the archive this evening.  I can recall looking at some of the
residential sidewall spray patterns (Tyco's website, I believe) and seeing
that they actually spray at a slightly upward angle.  I assumed that was the
reason section 8.10.7.1.2 was worded the way it is.  Time to do more
research.

Ed Kramer
Littleton, CO



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Wednesday, January 30, 2008 2:04 PM
To: [email protected]
Subject: RE: 13 residential obstructions

(1) You are correct. 8.10.7.1.2 (02) does read that way. However, if you
look at table 8.10.7.1.3 it is clear that the intent is you cannot have any
obstructions below the deflector within 8 feet. If the bottom of your soffit
is above the deflector, it can be used.

(2) I asked Tyco this question, (re. soffits along the far wall) sometime
back, as they copy this table in their installation manual. I asked them,
what if the obstructioon at the far wall is only 1/2" wide, like a
decorative moulding? They replied yes it is an obstruction as per NFPA, if
it is within 8 feet. As I requested this information in writing, I asked
whether they could reply in writing. Then they said that they wouldn't as it
is an NFPA requirement. Anyway having said that, this issue was discussed at
length in this forum, and the consensus (as per my judgement) was one needs
to use some reason when using this section.

Tony   

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: January 30, 2008 12:29 PM
To: [email protected]
Subject: RE: 13 residential obstructions

This was a serious question, I wasn't being sarcastic.  Really.  My hope is
that I'm missing something because I'd really like to use sidewalls on this
particular project.  So, anybody care to comment?

Ed Kramer
Littleton, CO

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Tuesday, January 29, 2008 2:32 PM
To: [email protected]
Subject: RE: 13 residential obstructions

This thread reminds me of a dilemma I tussled with last week.  In regards to
residential sidewalls, section 8.10.7.1.2 (02) says not to install
residential sidewalls within 8' of a light "or similar obstructions."  It
doesn't provide any exceptions, such as the light being only 4" deep and the
sidewall installed 6" down from the ceiling.  It simply says you can't do
it.  

Is a soffit along the wall opposite the sidewall considered a "similar
obstruction"?  I have a project where a 24" deep soffit is installed along 1
wall of the bedroom and along 1 wall of the living area (for ductwork).
Disregarding the soffits, sidewalls would work wonderfully.  If I consider
the soffit a "similar obstruction", that pretty much eliminates the use of
sidewalls.  Am I missing something?  Am I misinterpreting the intent of
8.10.7.1.2?

Ed Kramer
Littleton, CO

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to