Each building should be on a zone.  Each building should have its own
fire alarm panel.  Separate buildings, separate systems.  However, new
language in NFPA 13 was added to allow one building to feed another
building within certain guidelines.

Hope this helps,
John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, January 29, 2008 7:51 AM
To: [email protected]
Subject: Sprinkler Zones for Horizontal Exit Building

A single use structure has been divided into 3 buildings because of
occupancy and construction type issues related to the IBC.  Horizontal
exits are provided and this means the building cannot be evacuated
simultaneously using the stair widths available.

Question - Are separate sprinkler zones required for each building?  I
believe the answer is yes but I can't find a code reference that spells
this out in black and white.  It seems if the sprinkler zones cross over
the building boundary the fire alarm system will not be able to operate
the correct evacuation signals.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to