Bill,

If we were discussing a health care or detention and correctional occupancy,
I would say the zoning should definitely match the barrier arrangement.  The
intent being that you need to know which zone is in alarm to communicate
alarm sequences to occupants under a defend in place strategy.

If your example is a general evacuation, what difference would it make where
the fire was occurring?  All areas would receive a temporal 3 general evac
alarm.  Egress through a horizontal exit does not necessarily mean the
occupants should remain in the building. You mentioned construction type,
which leads me to presume you may have a fire wall creating a separate
building(s).  If that is the case, zones per building make sense as the
occupants in the adjacent building may not evacuate.

I don't think there is specific code language in either the IBC or LSC on
this issue.  It's something that needs to be integrated into the overall
fire evacuation strategy, marrying together life safety, fire alarm, and
sprinkler objectives.


Ray Schmid, P.E.
President 
Schmid & Associates, PC
Fire Protection Engineers
443-465-4206
[EMAIL PROTECTED]
 
This communication is confidential. This information may be privileged and
is intended for the exclusive use of the above named addressee(s). If you
are not the intended recipient(s), you are expressly prohibited from
copying, distributing, disseminating, or in any other way using any of this
information contained herein. If you have received this communication in
error, please contact the sender by telephone at (443) 465-4206 or respond
via e-mail and then permanently delete the original email and any copies.




-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, January 29, 2008 7:51 AM
To: [email protected]
Subject: Sprinkler Zones for Horizontal Exit Building

A single use structure has been divided into 3 buildings because of
occupancy and construction type issues related to the IBC.  Horizontal
exits are provided and this means the building cannot be evacuated
simultaneously using the stair widths available.

Question - Are separate sprinkler zones required for each building?  I
believe the answer is yes but I can't find a code reference that spells
this out in black and white.  It seems if the sprinkler zones cross over
the building boundary the fire alarm system will not be able to operate
the correct evacuation signals.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to