Carl, I am not sure of the definition of the word "supplemental" as used.

Bill pointed out that the stair widths are insufficient for simultaneous 
evacuation of the buildings.  Therefore, the horizontal exits are required 
exits.

We seem to agree that there should be three zones.  I am not sure you agree 
that the notification appliances cannot be operated in other than the fire 
building.
 
Ed Vining
  4819 John Muir Rd
  Martinez CA 94553
  925-228-8792
  [EMAIL PROTECTED]

----- Original Message ----
From: "Chappell, Carl" <[EMAIL PROTECTED]>
To: [email protected]
Sent: Friday, February 1, 2008 2:46:36 PM
Subject: RE: Sprinkler Zones for Horizontal Exit Building


>From what we have experienced, the intent of the horizontal exit is to
be supplemental to the stairs and other egress components.  However, as
currently done the horizontal exit also acts as an audible zone
boundary.  This implies that the notification appliances connected to
the fire alarm system are also zoned to match.  Essentially the fire
alarm (detection and notification), sprinklers and smoke management (if
provided) should be zoned to match the physical characteristics of the
building(s).  

 
 
Carl Chappell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed
 Vining
Sent: Friday, February 01, 2008 8:42 AM
To: [email protected]
Subject: Re: Sprinkler Zones for Horizontal Exit Building

The fire can be in any of the three buildings.  If I am standing in a
corridor by a horizontal exit and hear the alarm, I look up at the exit
sign and go through that exit.  That exit sign just told me I was going
to a safe place.  It can very well send me into the fire area.
 
Ed Vining
  4819 John Muir Rd
  Martinez CA 94553
  925-228-8792
  [EMAIL PROTECTED]

----- Original Message ----
From: Ray Schmid <[EMAIL PROTECTED]>
To: [email protected]
Sent: Friday, February 1, 2008 6:20:00 AM
Subject: RE: Sprinkler Zones for Horizontal Exit Building


Bill,

If we were discussing a health care or detention and correctional
 occupancy,
I would say the zoning should definitely match the barrier arrangement.
  The
intent being that you need to know which zone is in alarm to
 communicate
alarm sequences to occupants under a defend in place strategy.

If your example is a general evacuation, what difference would it make
 where
the fire was occurring?  All areas would receive a temporal 3 general
 evac
alarm.  Egress through a horizontal exit does not necessarily mean the
occupants should remain in the building. You mentioned construction
 type,
which leads me to presume you may have a fire wall creating a separate
building(s).  If that is the case, zones per building make sense as the
occupants in the adjacent building may not evacuate.

I don't think there is specific code language in either the IBC or LSC
 on
this issue.  It's something that needs to be integrated into the
 overall
fire evacuation strategy, marrying together life safety, fire alarm,
 and
sprinkler objectives.


Ray Schmid, P.E.
President 
Schmid & Associates, PC
Fire Protection Engineers
443-465-4206
[EMAIL PROTECTED]




-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, January 29, 2008 7:51 AM
To: [email protected]
Subject: Sprinkler Zones for Horizontal Exit Building

A single use structure has been divided into 3 buildings because of
occupancy and construction type issues related to the IBC.  Horizontal
exits are provided and this means the building cannot be evacuated
simultaneously using the stair widths available.

Question - Are separate sprinkler zones required for each building?  I
believe the answer is yes but I can't find a code reference that spells
this out in black and white.  It seems if the sprinkler zones cross
 over
the building boundary the fire alarm system will not be able to operate
the correct evacuation signals.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)