See 13:A.8.16.5.2. (02 edition) It came out of NFPA 14 though not
sure of the edition (Steve any help on that?). It is not longer a 14
issue so it was deleted in the 07 edition of 13. There are other
components to go along with such arrangements, check valves in both
feeds as well as a new issue whereby signs indicating the presence of
the other water supply source on both control valves.
Roland
On Feb 12, 2008, at 2:29 PM, Brian wrote:
Hello,
I've got a project requiring a standpipe on either side of a 4
story building. Both of these standpipes are being planned as feeds
for the fire sprinkler system.In other words, at each level the
fire sprinkler system will tap off each standpipe so that it can be
looped at each floor. I had someone tell me that this was against
code and that you could tap off each standpipe but they could not
be connected (ie. looped). When I questioned which code states this
they didn't have an answer. I have never come across a code stating
this could not be done - afterall, loops are legitimate system
types defined in NFPA #13. In the past we would put a sign at each
control valve stating that each floor is controlled by two control
valves at each stairwell and everyone was alright with this.
Has anyone ever heard of such a code?
Thanks,
-B-
---------------------------------
Never miss a thing. Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)