I did this back in 1978 at a Stonybrook Manor in York, PA. A young man named
Jeff Mattern was FM's local field engineer, I think he received a few
promotions and is trying to retire (Joe, maybe you could offer some advice?)

My recollection was that this practice was stopped by a change in the code,
shortly after the job- so maybe in if you have a 1981 #13, you could look in
the margin for the changed section? Including time to dig one out, it'd
probably take less time, it's maybe a 150 page document.

You mention loops as a legitimate system design; I take issue with not the
loop, but the application. How many "looped" systems have two connections to
the water supply and two risers?

The biggest issue to stop you would be the flow switch, if you are zoning by
floor. Suppose a 1/2" head goes off in the middle of the floor, and 1/2 the
water comes this way, half that way, and neither exceeds the amount needed
to trip the flow switch? Trust me, you don't want the elevator not working
to be your flow indicator!!!

You may be echoing what I recall Marriott's Module 14 now shows for
high-rises, none of the Marriotts we've done have been hi-rise. That may be
a source of ammo to support your effort for efficiency.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Tuesday, February 12, 2008 5:29 PM
To: [email protected]
Subject: Combined Sprinkler/Standpipes Systems LOOPED

Hello,
   
  I've got a project requiring a standpipe on either side of a 4 story
building. Both of these standpipes are being planned as feeds for the fire
sprinkler system.In other words, at each level the fire sprinkler system
will tap off each standpipe so that it can be looped at each floor. I had
someone tell me that this was against code and that you could tap off each
standpipe but they could not be connected (ie. looped). When I questioned
which code states this they didn't have an answer. I have never come across
a code stating this could not be done - afterall, loops are legitimate
system types defined in NFPA #13. In the past we would put a sign at each
control valve stating that each floor is controlled by two control valves at
each stairwell and everyone was alright with this.
   
  Has anyone ever heard of such a code?
   
  Thanks,
   
  -B-
   