Beat me to it.   So long as each sprinkler connection is furnished with
a check valve, the looped sprinkler mains will not serve in any way as a
redundant interconnection.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Robert
Sent: Tuesday, February 12, 2008 2:52 PM
To: [email protected]
Subject: RE: Combined Sprinkler/Standpipes Systems LOOPED

 
6.2.8.3  Where sprinkler system piping supplied by a combined system is
supplied by more than one standpipe ("loop" or "dual feed" design), a
sign
shall be located at each dual or multiple feed connection to the
combination
system standpipe to indicate that in order to isolate the sprinkler
system
served by the control valve, an additional control valve or valves at
other
standpipes shall be shut off.   NFPA 14




-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Tuesday, February 12, 2008 4:29 PM
To: [email protected]
Subject: Combined Sprinkler/Standpipes Systems LOOPED

Hello,
   
  I've got a project requiring a standpipe on either side of a 4 story
building. Both of these standpipes are being planned as feeds for the
fire
sprinkler system.In other words, at each level the fire sprinkler system
will tap off each standpipe so that it can be looped at each floor. I
had
someone tell me that this was against code and that you could tap off
each
standpipe but they could not be connected (ie. looped). When I
questioned
which code states this they didn't have an answer. I have never come
across
a code stating this could not be done - afterall, loops are legitimate
system types defined in NFPA #13. In the past we would put a sign at
each
control valve stating that each floor is controlled by two control
valves at
each stairwell and everyone was alright with this.
   
  Has anyone ever heard of such a code?
   
  Thanks,
   
  -B-
   

       
---------------------------------
Never miss a thing.   Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to