>From NFPA 14: A-4-2.5.2 Combined automatic sprinkler and standpipe risers should not be interconnected by sprinkler system piping.
This is in the appendix so may not be adopted in your area. But, this may be were they were getting it. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Sent: Tuesday, February 12, 2008 3:29 PM To: [email protected] Subject: Combined Sprinkler/Standpipes Systems LOOPED Hello, I've got a project requiring a standpipe on either side of a 4 story building. Both of these standpipes are being planned as feeds for the fire sprinkler system.In other words, at each level the fire sprinkler system will tap off each standpipe so that it can be looped at each floor. I had someone tell me that this was against code and that you could tap off each standpipe but they could not be connected (ie. looped). When I questioned which code states this they didn't have an answer. I have never come across a code stating this could not be done - afterall, loops are legitimate system types defined in NFPA #13. In the past we would put a sign at each control valve stating that each floor is controlled by two control valves at each stairwell and everyone was alright with this. Has anyone ever heard of such a code? Thanks, -B- --------------------------------- Never miss a thing. Make Yahoo your homepage. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ NOD32 2870 (20080212) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)