Anyone see any problems with this: Having a 4" RP Backflow at the base of riser 
and then tapping an antifreeze system off of the wet system but instead of an 
expansion chamber (as required by code for a double check) running the old 
style a/f 5ft loop off of this. Reasoning is since an RP type backflow ports 
when overpressurized on system side the a/f system can still expand through the 
loop like in the good ol' days. 
  
It seems NFPA#13 only requires the expansion chamber since it would be 
impossible for the antifreeze to otherwise expand since everything is 'locked' 
in place by the double check. However with an RP backflow it would allow the 
backwards movement of water neccessary for expansion and the loop would perform 
it's duties of acting as a container for the antifreeze and not be ported out 
with the water. 
   
  We had this arrangement ok'd by an AHJ in the past but want to see if there 
is something we're overlooking.
   