"Now, a couple of jurisdictions are requiring RPZ's instead of the double
checks anytime you have any type of antifreeze; toxic or non. The way
they've been interpreting the code"

Brian,

The 2006 National Standard Plumbing Code provides the requirement for RPZ
when antifreeze is present (type not stipulated) or an FDC is present (the
1700ft distance to non potable source has been eliminated) on a water based
fire protection system.

Please explain the error of our way as AHJ's. If theres some term, phrase or
wiggle room in the NSPC's backflow requirements I'd like to know so I can
pass it along to our plumbing inspectors. As the fire protection subcode
official I'm responsible for approval and make sure a RPZ BFP is included in
the calc's where stipulated by the NSPC knowing well that the plumbing
inspectors going to require it.

If not the only way its going away is to change the NSPC.

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Tuesday, February 26, 2008 7:17 PM
To: [email protected]
Subject: RE: RP Backflow with Antifreeze Loop

Your quote below is hitting the nail on the head. It's like a light bulb
went on for the first time - probably the first time in a long time ;-)
Locally the norm is EVERY sprinkler system, antifreeze or not, gets a double
check on the fire line; usually at the base of riser inside the building.
Now, a couple of jurisdictions are requiring RPZ's instead of the double
checks anytime you have any type of antifreeze; toxic or non. The way
they've been interpreting the code - myself included since I've worked in
these jurisdictions for so long, is that even though the RPZ is at the riser
you would need to have an expansion chamber with say, a check valve before
it - or a seperate RPZ & exp. chamber just for the a/f system and another at
the riser (overkill galore). But so, you're saying the proper interpretation
would not require an expansion chamber in this case? Picture a little
warehouse no frills riser, it comes in at a 6X11" flange to a backflow prev.
then to guages, main
 drain, flow switch, then above flow switch an outlet to a a/f loop. This
would not require an expansion chamber because the BFP is not between the
a/f loop and the wet connection? Is this right?
   
  thx,
  b
  

Ed Kramer <[EMAIL PROTECTED]> wrote:
  " Note that you're still allowed to have a BFP
(double-check or otherwise) as long as its not in the connection between the
wet system and the AFL."

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Brian
> Sent: Tuesday, February 26, 2008 2:27 PM
> To: [email protected]
> Subject: RP Backflow with Antifreeze Loop
> 
> Anyone see any problems with this: Having a 4" RP Backflow at the base
> of riser and then tapping an antifreeze system off of the wet system but
> instead of an expansion chamber (as required by code for a double check)
> running the old style a/f 5ft loop off of this. Reasoning is since an RP
> type backflow ports when overpressurized on system side the a/f system
> can still expand through the loop like in the good ol' days.
> 
> It seems NFPA#13 only requires the expansion chamber since it would be
> impossible for the antifreeze to otherwise expand since everything is
> 'locked' in place by the double check. However with an RP backflow it
> would allow the backwards movement of water neccessary for expansion and
> the loop would perform it's duties of acting as a container for the
> antifreeze and not be ported out with the water.
> 
> We had this arrangement ok'd by an AHJ in the past but want to see if
> there is something we're overlooking.
> 
> thx,
> 
> 
> 
> 
> ---------------------------------
> Looking for last minute shopping deals? Find them fast with Yahoo!
> Search.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to