Your quote below is hitting the nail on the head. It's like a light bulb went on for the first time - probably the first time in a long time ;-) Locally the norm is EVERY sprinkler system, antifreeze or not, gets a double check on the fire line; usually at the base of riser inside the building. Now, a couple of jurisdictions are requiring RPZ's instead of the double checks anytime you have any type of antifreeze; toxic or non. The way they've been interpreting the code - myself included since I've worked in these jurisdictions for so long, is that even though the RPZ is at the riser you would need to have an expansion chamber with say, a check valve before it - or a seperate RPZ & exp. chamber just for the a/f system and another at the riser (overkill galore). But so, you're saying the proper interpretation would not require an expansion chamber in this case? Picture a little warehouse no frills riser, it comes in at a 6X11" flange to a backflow prev. then to guages, main drain, flow switch, then above flow switch an outlet to a a/f loop. This would not require an expansion chamber because the BFP is not between the a/f loop and the wet connection? Is this right? thx, b
Ed Kramer <[EMAIL PROTECTED]> wrote: " Note that you're still allowed to have a BFP (double-check or otherwise) as long as its not in the connection between the wet system and the AFL." Ed Kramer Littleton, CO > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Brian > Sent: Tuesday, February 26, 2008 2:27 PM > To: [email protected] > Subject: RP Backflow with Antifreeze Loop > > Anyone see any problems with this: Having a 4" RP Backflow at the base > of riser and then tapping an antifreeze system off of the wet system but > instead of an expansion chamber (as required by code for a double check) > running the old style a/f 5ft loop off of this. Reasoning is since an RP > type backflow ports when overpressurized on system side the a/f system > can still expand through the loop like in the good ol' days. > > It seems NFPA#13 only requires the expansion chamber since it would be > impossible for the antifreeze to otherwise expand since everything is > 'locked' in place by the double check. However with an RP backflow it > would allow the backwards movement of water neccessary for expansion and > the loop would perform it's duties of acting as a container for the > antifreeze and not be ported out with the water. > > We had this arrangement ok'd by an AHJ in the past but want to see if > there is something we're overlooking. > > thx, > > > > > --------------------------------- > Looking for last minute shopping deals? Find them fast with Yahoo! > Search. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) --------------------------------- Looking for last minute shopping deals? Find them fast with Yahoo! Search. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)