The expansion chamber is to avoid excessive pressure due to long term
temperature changes (that being between summer and winter). Yea, I
am good at stating the obvious. 13 requires one when you install a
BFP on a small antifreeze systems that are sub-system to a wet pipe
(since large changes are expected). Note the wording is when a BFP
is in the connection between the antifreeze system and the wet pipe
system. So what about when it's just one big antifreeze system.
When we put BFP on a wet system we do not require an expansion
chamber (as stated earlier) due to all the trapped air providing room
for expansion. The problem with that is that the BFP can interfere
with the alarm switch and the fix is to purge the trapped air (to the
point of installing an air relief valve). The fact that these are
mostly in occupied areas where the temperature swings are not as
great helps. Probably the same thing can be said for big standalone
antifreeze systems. You hopefully don't get big temperature swings
in freezers. As such, one can reasonable argue that large standalone
antifreeze systems do not need an expansion chamber. The other side
of that debate is that considering how ugly it gets when you break
any pipe but even more so in a freezer, do you want to chance it?
Roland
On Feb 26, 2008, at 6:03 PM, Brian wrote:
John, I'm not questioning the backflow requirement - I know this is
required by the plumbing codes as backflow prevention has
absolutely nothing to do with fire protection (ie. it's not a fire
protection device). Your quote cuts me off... I'm referring to
local AHJ's requiring expansion chambers when it looks like it's
not neccessary since the a/f interface in the scenario I described
is not between the loop and the connection to wet system. That's all.
B