23 sqft per head in a light hazard corridor should be enough. With 7 psi
you have a 0.66 density.  The skylight section is poorly written. We ran
into a project with four 2'x2' skylights two feet apart. The letter of
the standard would require a head in each but we left them out and the
AHJ didn't comment.

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Margaret
Zabel
Sent: Tuesday, February 26, 2008 5:03 PM
To: Sprinkler Forum
Subject: Omitting sprinklers from skylights

I have two 4' x 4' skylights separated by 9' of ceiling/structure
(located at approx. +13') in a 5'
wide corridor.  Due to the layout of the skylights and one additional
obstruction (an architectural "bridge"
located at approx. +8' to +10'), there will be four sprinklers at the
ceiling/structure level into which the skylights are framed. Two of
these sprinklers are located between the skylights.  The bridge requires
one sprinkler below it.  This bridge/obstruction will NOT impede heat
flow from one skylight to the next.  

Do you see any huge problems if I suggest to the AHJ that sprinklers
might be omitted from these skylights?
 If these two sprinklers are not omitted, there will be (7) sprinklers
protecting the floor area along a 32' long corridor.

Thank you for your thoughts,

Margaret Zabel
BFP Fire Protection
home office:  510-227-5337
[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to