23 sqft per head in a light hazard corridor should be enough. With 7 psi you have a 0.66 density. The skylight section is poorly written. We ran into a project with four 2'x2' skylights two feet apart. The letter of the standard would require a head in each but we left them out and the AHJ didn't comment.
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Margaret Zabel Sent: Tuesday, February 26, 2008 5:03 PM To: Sprinkler Forum Subject: Omitting sprinklers from skylights I have two 4' x 4' skylights separated by 9' of ceiling/structure (located at approx. +13') in a 5' wide corridor. Due to the layout of the skylights and one additional obstruction (an architectural "bridge" located at approx. +8' to +10'), there will be four sprinklers at the ceiling/structure level into which the skylights are framed. Two of these sprinklers are located between the skylights. The bridge requires one sprinkler below it. This bridge/obstruction will NOT impede heat flow from one skylight to the next. Do you see any huge problems if I suggest to the AHJ that sprinklers might be omitted from these skylights? If these two sprinklers are not omitted, there will be (7) sprinklers protecting the floor area along a 32' long corridor. Thank you for your thoughts, Margaret Zabel BFP Fire Protection home office: 510-227-5337 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)