You need to discuss the issue with the AHJ but go armed with some
ammo (such as why the 10 ft requirement is there). I did an article
for the NFPA Journal in 2004 discussing just this issue (a copy is on
our web site, link is below).
http://www.firesprinkler.org/techservices/articles/
ceilingpoketsnfpa04.pdf
Roland
On Feb 26, 2008, at 4:02 PM, Margaret Zabel wrote:
I have two 4' x 4' skylights separated by 9' of
ceiling/structure (located at approx. +13') in a 5'
wide corridor. Due to the layout of the skylights and
one additional obstruction (an architectural "bridge"
located at approx. +8' to +10'), there will be four
sprinklers at the ceiling/structure level into which
the skylights are framed. Two of these sprinklers are
located between the skylights. The bridge requires
one sprinkler below it. This bridge/obstruction will
NOT impede heat flow from one skylight to the next.
Do you see any huge problems if I suggest to the AHJ
that sprinklers might be omitted from these skylights?
If these two sprinklers are not omitted, there will
be (7) sprinklers protecting the floor area along a
32' long corridor.
Thank you for your thoughts,
Margaret Zabel
BFP Fire Protection
home office: 510-227-5337
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)